cjashower said:
6mm feed from the consumer unit (fitted with Memshield 2 RCCB 63A - was the feed for a 8Kw shower).
Never mind the RCCB, what's the rating of the MCB?
I am now putting in a new 10.5KW shower. I am using twin earth 10mm and going back to the same consumer unit. Am I correct in believing that I can connect to the same Memshield 2 RCCB? It is a Memera 2000 unit.
No, you are not correct - firstly you aren't connecting to the RCCB, you are connecting to the MCB, and secondly whatever was there for an 8kW shower on a 6mm² cable will not do for a 10.5kW shower.
cjashower said:
Thank you FWL_Engineer and breezer. I am a little confused. What I had intended was to take the 10mm from the shower back to the rccb and the 6 mm from the pump to the rccb.
No - this will not do at all - after you've replaced the MCB with a 45A one for the shower the protection will be inadequate for a 6mm² cable.
I think you need to read this:
http://www.diynot.com/forums/viewtopic.php?p=81696#81696
what I think you are suggesting is that I take only the 10mm back to the rccb and connect the pump via a spur using 6mm cable. Is this correct.
You don't need 6mm² to supply the pump - it probably only draws a few amps. What is it rated at?. You
do need the supply side of the FCU to be fed via preferably 10mm², but a short length of 6mm² in free air where it is unlikely to be disturbed would do. But have you thought about how and where you are going to join 2 x 10mm² or a 10mm² & 6mm² cables together? You'll not get both into the same terminals of an FCU....
I assume I would want some form of switch so that I could ensure that only the shower or pump could be used at one time. If this is correct what sort of switch and where would I have to position it?
You don't need a switch - as you said, they won't be on together, and even if they are, the additional load of the pump is probably of no importance. If you do want one, you'll need a DP changeover switch rated at at least 45A, positioned in Zone 3 or outside the zones, but be warned - they don't look too good from a domestic decor POV...
Are you sure that you know enough to be doing electrical work?