Have problem with boiler noise.
Potterton Kingfisher II RS60 floor standing.
I done significant checks on the system as follows:
Cleaned system with Fernox super concentrate
Flushed
Bled
Added inhibitor
Flushed
Bled
Cleaned with Sentinel X200
Added inhibitor.
Bled
Gravity HW, pumped CH, TRV on all but 2 RADS, Only thermostat is boiler main stat. Pump is on the return leg next to the boiler.
Symptoms:-
Boiler makes hissing noise when getting to temperature, also clanks and bangs.
This is much worse when CH is on.
When only on HW, the thermostat cuts out just after the boiler starts hissing.
When HW and Ch the boiler makes the clanking banging noises before the thermostat cuts out.
There is no air in the system.
The circulation is very good and pump has been tested on all 3 speeds with no effect on the noise.
All TRVs and lock shields have been opened fully to try and increase flow with no effect.
If I turn down the boiler stat the water temperature does reduce but I still get the noises, although the cycle time becomes much longer.
If the stat is on number 4 and CH and HW are on the boiler starts to make the noises, if I then stop the pump by jamming the impeller the thermostat cuts the boiler out almost immediately. This is as if the HW circuit is at temperature but the CH circuit is still below the thermostat setting.
If the CH circuit is at temperature then thermostat still seems to keep the boiler running longer thus make the load noises as the boiler starts to boil the water.
A couple of questions.
The thermostat tail looks like it goes into the middle of the boiler. What temperature is this measuring, water return of CH, HW or both?
Could the problem be with the thermostat not cutting out at the correct temp? I thought when a thermostat went the boiler would either not cut in or would not cut out.
Or is the boiler at the last stages of its life?
This is a cast iron boiler that is 9 years old.
The system when flushed had no sludge and the water was very clean.
No Rads have black crap.
Any help on this would be very helpful as I have not had much sleep due to the noise.
Flushed
Bled
Added inhibitor
Flushed
Bled
Added inhibitor.
Bled
Symptoms:-