The system is about 9 years old, fitted in a domestic residence, and has worked fine up until a few days ago. I believe it is a Y Plan system. It has a tank in the airing cupboard and a T shaped valve fed from a pump. One side of the valve goes to the tank, the other to the 14 radiators. Boiler is a glowworm Micron 60FF.
Hot water is fine.
When I call CH the boiler does not fire up (programmer light comes on for CH and room stat is turned up).
If I move the valve lever over to the RHS, the boiler fires up and the rads start to get warm. Not sure if this is the valve midpoint or it is in the CH position.
I have measured the voltage on the white wire in the junction box in the airing cupboard and this goes to 240VAC when the room stat is set to max, and 0V when set to min.
I therefore conclude that the non mechanical part of 3 port valve is at fault. However, I pulled the head off the valve and measured the motor coil and it is 2K ohms. Which looks like a good motor to me.
I know the fault is not the boiler (HW OK), not the programmer or room stat (240V called from stat).
How likely is it that this is the 3 port valve, and can I get away without changing the mechanical part. There are no model names on the valve so I cant identify it for replacement purposes (motor has synchron on it though).
I am reasonably technically able, and have done some plumbing in the passed, but am concerned about having to drain down and remove air locks etc, so would prefer not to change the mechanical part if possible. There are isolators on the Tank and CH sides of the valve which might help.
Advice sought please. What should I do next.
Hot water is fine.
When I call CH the boiler does not fire up (programmer light comes on for CH and room stat is turned up).
If I move the valve lever over to the RHS, the boiler fires up and the rads start to get warm. Not sure if this is the valve midpoint or it is in the CH position.
I have measured the voltage on the white wire in the junction box in the airing cupboard and this goes to 240VAC when the room stat is set to max, and 0V when set to min.
I therefore conclude that the non mechanical part of 3 port valve is at fault. However, I pulled the head off the valve and measured the motor coil and it is 2K ohms. Which looks like a good motor to me.
I know the fault is not the boiler (HW OK), not the programmer or room stat (240V called from stat).
How likely is it that this is the 3 port valve, and can I get away without changing the mechanical part. There are no model names on the valve so I cant identify it for replacement purposes (motor has synchron on it though).
I am reasonably technically able, and have done some plumbing in the passed, but am concerned about having to drain down and remove air locks etc, so would prefer not to change the mechanical part if possible. There are isolators on the Tank and CH sides of the valve which might help.
Advice sought please. What should I do next.