One of my lads rang me today to say he had found a Zs of 243.5 on a ring final.
Having ascertained the supply was PME, the earth link was missing and the gas & water pipes were bonded to 7671, I instructed him to leave a 16mm2 earth tail and ring the customer's DNO to get the link installed.
The (annoyed) customer rang him back to say the DNO refused to connect without a cert.
Can they do this? Especially as they should have provided an earth connection in the first place....I mean, PME (or any system, come to that) without earth is an accident waiting to happen.
Edit: I have just phoned them, and they see no reason why it cannot be done, but say that if the earth connection has been tampered with, to reinstate it would be chargeable work.