S
scotsparky
No RF if i see a 2.5 as a Main Earth i will code 1 it.
How can you justify giving a code 1 to an installation that complies fully with BS 7671 2008?
No RF if i see a 2.5 as a Main Earth i will code 1 it.
Where, in a TT system, disconnection is achieved by an overcurrent protective device and PE bonding is connected to all ex-c-p's within the installn in accordance with 411.3.1.2, the max disc. times applicable to TN system may be used. In other words, you can scrap the 0.2s and use 0.4s instead.
Where, in a TT system, disconnection is achieved by an overcurrent protective device and PE bonding is connected to all ex-c-p's within the installn in accordance with 411.3.1.2, the max disc. times applicable to TN system may be used. In other words, you can scrap the 0.2s and use 0.4s instead.
Most TT systems require RCDs to provide disconnection as opposed to overcurrent protective devices.
Think I just about got my head round it! I could have probably written my post a bit clearer though.Yep, (it is acceptable to bury a 2.5mm conductor in the ground as long as it is protected against mechanical damage.)
59/60