For a Halstead Quattro Combi (LPG).
Overheat thermostat ok, circuit closed, Pump overrun thermostat working, closed circuit common to one, but not the other. Pump operating fine, a number of clicks suggesting microswitches ok.
Live power getting to Ignition board, but nothing getting to fan - 230V supply terminals dead to fan at fan end and on ignition board, even on fire-up, therefore no ignition without air flow getting to the pressure switch. I intend to test ignition soon, by providing the fan with its manual switched power supply.
Some suggest there's a flow switch on the pump to trigger the fan, but I cannot find this here (Grundfos 15-60 pump), so most likely it is the fan relay on the ignition board. How do I test this?
I want to be certain the fault is on the Ignition Board, rather than the Control Board.
There are four relays on this board (Honeywell 54561 D1001 upgraded to D1019 when replaced in 2007).
When firing up after replacing diverter valve, I inadvertantly pulled off the lead to the pump (kept control unit cover in place when water spilling about), got a humming sound and the ignition sparked. No gas then, since I turned that off until I was sure the system was purged of air. Switched off sharpish to find out what I'd done.
Could that have burned out a relay?
If so, can these be replaced individually or will I need an exchange board?
Overheat thermostat ok, circuit closed, Pump overrun thermostat working, closed circuit common to one, but not the other. Pump operating fine, a number of clicks suggesting microswitches ok.
Live power getting to Ignition board, but nothing getting to fan - 230V supply terminals dead to fan at fan end and on ignition board, even on fire-up, therefore no ignition without air flow getting to the pressure switch. I intend to test ignition soon, by providing the fan with its manual switched power supply.
Some suggest there's a flow switch on the pump to trigger the fan, but I cannot find this here (Grundfos 15-60 pump), so most likely it is the fan relay on the ignition board. How do I test this?
I want to be certain the fault is on the Ignition Board, rather than the Control Board.
There are four relays on this board (Honeywell 54561 D1001 upgraded to D1019 when replaced in 2007).
When firing up after replacing diverter valve, I inadvertantly pulled off the lead to the pump (kept control unit cover in place when water spilling about), got a humming sound and the ignition sparked. No gas then, since I turned that off until I was sure the system was purged of air. Switched off sharpish to find out what I'd done.
Could that have burned out a relay?
If so, can these be replaced individually or will I need an exchange board?