Fitted my neighbour a 28Cdi 3 years ago, used cleanser and inhibitor at the time.
Problems are when on hot water it sounds like it is overheating, chug chug chug and nearly banging, (OH stat isn't cutting in though) when on CH it gets noisy when getting near cut off temp as well.
Gas rate is correct and according to flame and manometer seems to modulate on both HW & CH, had DHW exchanger out flushed through and not blocked or really very dirty, hot water temp to taps is ok, had pump out and cleaned, shaft ok, downstairs rads get hot so pump working ok, bathroom rad and byepass open.
Ohms reading on both sensors approx 2 ohms when hot, supposed to be between 1 and 30 so taking this to be ok as wouldn't suppose "both" sensors would be duff.
Thinking of taking off the gas to water HE off to flush out, anybody got any ideas on best way of cleaning and what with or any other ideas whats wrong with the beast.
Problems are when on hot water it sounds like it is overheating, chug chug chug and nearly banging, (OH stat isn't cutting in though) when on CH it gets noisy when getting near cut off temp as well.
Gas rate is correct and according to flame and manometer seems to modulate on both HW & CH, had DHW exchanger out flushed through and not blocked or really very dirty, hot water temp to taps is ok, had pump out and cleaned, shaft ok, downstairs rads get hot so pump working ok, bathroom rad and byepass open.
Ohms reading on both sensors approx 2 ohms when hot, supposed to be between 1 and 30 so taking this to be ok as wouldn't suppose "both" sensors would be duff.
Thinking of taking off the gas to water HE off to flush out, anybody got any ideas on best way of cleaning and what with or any other ideas whats wrong with the beast.