Layout: My combi condensing boiler (Ideal HE24) is located downstairs one end of the house. There’s 22mm pipe off the boiler tee’d , one side down to 15mm to feed 2 rads downstairs total about 4kw, the other 22mm shooting off upstairs to feed the upstairs and the downstairs at the other side of the house, approx loading upstairs 5kw and remaining down stairs 4.5kw.
The 22mm runs the length of the landing upstairs approx 9m with braches off feeding upstairs and reduces down to 15mm dropping downstairs disappearing under the concrete floor (which then changes from copper to plastic) which feeds 4 rads the farthest being approx 9m in pipe at 1.5kw from this down drop.
The problem I have is to get the heat to the rads downstairs the opposite end of the house to the boiler is I have to throttle (balance) the rads closer to the boiler down via locksheild, to the extent that the rads closet to the boiler upstairs (in the bedrooms which is the worst place to have that noise) you can hear the water forcing it’s way through the lockshield valves (plus any debris flowing through the system lodges here, rattling adding to the problem).
Typically the lock shields close to the boiler are open about ½ to 1 turn. Yes we have TRVs but it’s not that end the rad the noise is coming from and it happens when the system/house is just warming.
My first thought was the pipe sizing was wrong but doing some rough calculations (using a little more info than presented here)Using temp drop of 20oc I get my index circuit (exclude boiler and rads) to around 0.56m, and my bedroom circuits to around 0.15m, as I’m relatively new to plumbing this doesn’t seem excessive??
Am I barking up the wrong tree, would hate to rip pipework out (which is not the best installed pipe layout anyhow) if I don’t have to.
Any ideas??
The 22mm runs the length of the landing upstairs approx 9m with braches off feeding upstairs and reduces down to 15mm dropping downstairs disappearing under the concrete floor (which then changes from copper to plastic) which feeds 4 rads the farthest being approx 9m in pipe at 1.5kw from this down drop.
The problem I have is to get the heat to the rads downstairs the opposite end of the house to the boiler is I have to throttle (balance) the rads closer to the boiler down via locksheild, to the extent that the rads closet to the boiler upstairs (in the bedrooms which is the worst place to have that noise) you can hear the water forcing it’s way through the lockshield valves (plus any debris flowing through the system lodges here, rattling adding to the problem).
Typically the lock shields close to the boiler are open about ½ to 1 turn. Yes we have TRVs but it’s not that end the rad the noise is coming from and it happens when the system/house is just warming.
My first thought was the pipe sizing was wrong but doing some rough calculations (using a little more info than presented here)Using temp drop of 20oc I get my index circuit (exclude boiler and rads) to around 0.56m, and my bedroom circuits to around 0.15m, as I’m relatively new to plumbing this doesn’t seem excessive??
Am I barking up the wrong tree, would hate to rip pipework out (which is not the best installed pipe layout anyhow) if I don’t have to.
Any ideas??