Hi,
I have a SIME badged Potterton profile 100e.
Every morning as my electronic Programmer switches off the boiler therm stat reset button trips and i have to go down and reset it. (The button under the boiler). It basically does it as well with +1hr or turning the water off manually,
We have replaced the overheat stat and the pump over run stat. We also found the gas supply has been set to the wrong flow and altered it. Neither of these things has changed the problem. The ONLY thing that alters is it very odd. If you change the stat on the hot water cylinder in the bathroom down to 50 it doesn't reset! Im not sure why altering the temp of cylinder would affect the boiler.
it does not reset on the central heating.
Am at a total loss as r two corgi guys helping me.
I have a SIME badged Potterton profile 100e.
Every morning as my electronic Programmer switches off the boiler therm stat reset button trips and i have to go down and reset it. (The button under the boiler). It basically does it as well with +1hr or turning the water off manually,
We have replaced the overheat stat and the pump over run stat. We also found the gas supply has been set to the wrong flow and altered it. Neither of these things has changed the problem. The ONLY thing that alters is it very odd. If you change the stat on the hot water cylinder in the bathroom down to 50 it doesn't reset! Im not sure why altering the temp of cylinder would affect the boiler.