Bit confused on this one, burner will fire perfectly from cold until the boiler stat stops calling for heat, then it cools until the stat calls for heat again, then it purges and attempts ignition but goes to lockout. It won't fire again if the lockout button is pressed until about 45mins later when it has cooled then starts again perfectly.
It's a warmflow 120he condensing boiler with a riello rdb 2.2 oil burner.
240v to the control box.
New pump was fitted recently.
Oil supply is fine.
Solenoid valve itself seems fine, not seized and all of the oil ports are clear.
Electrodes are gapped correctly.
Nozzle isn't coked up.
Photocell is good, getting 300ohms with light & infinity when dark.
Replaced the solenoid coil and its wiring.
I'm guessing the control box. Again the burner fires up perfectly when pressing the lockout button but only when it is cool, but will not fire at all when warm.
Any advise or guidance is very much appreciated.