Each edition of the regulations gives a date after which DESIGNS must follow it, it is permitted to actually commission a new house to old regulations if the old regulations were in force at the time it was designed.
The code 4 does not comply with current regulations if designed today was removed from the EICR as it was considered unhelpful. The problem code is code C2 = Potentially dangerous, no one really questions the dangerous C1 code, or improvements recommended, code c3, and the code FI means for some reason no access.
So the electrical safety council says
however although the BS7671 is not retrospective, it is tied to CENELEC and HSE rules which may be, however the inspector does not sign to say legal, he signs to say not potentially dangerous, so even if it does not comply with a law he can still give an item a code C3, he is saying if the installation is safe to use, not if it complies.
However what
@motorbiking and
@plugwash say is true, the law is poorly written, it says BS7671:2018 should be followed, it says the DNO equipment is NOT part of the inspection where the IET guidelines says it is, and that in-service electrical equipment not designed to be moved is part of the inspection where all the IET stuff says this is done under inspection and testing of in service equipment (PAT testing) completely independent of the installation, the installation is wires, fuses and other overload devices, switches etc., but not anything that uses power, so chandelier is included but not the bulbs.
There are of course items which span the divide, the fluorescent lamp fitting the whole lamp should come under the PAT testing, but in real terms this would be rather hard, so all electrical items should be tested, and it is normally agreed between electricians that extractor fans, lights, immersion heaters, boilers etc, either are done at same time as the EICR or are under a maintenance contract. Common for boilers, fridges, freezers, vending machines etc. to be under a maintenance contract.
Remember the EICR is designed for all, not just domestic, so the rules have to be designed to work in commercial premises as well as domestic. And likely the vending machine is hired or rented and the in house electrician has not got keys to be able to open it and test it, so some one is considered as the manager and has to ensure there is paperwork in place for all items.
The idea of modifying what comes under the test simply does not work, as the same test and inspection also covers commercial property.
So we do get in the laws a glossary of terms.
“consumer’s installation” means the electric lines situated upon the consumer’s side of the supply terminals together with any equipment permanently connected or intended to be permanently connected thereto on that side;
“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018(3);
“qualified person” means a person competent to undertake the inspection and testing required under regulation 3(1) and any further investigative or remedial work in accordance with the electrical safety standards;
The result is the laws to not actually line up with the regulations. And we do have a problem, under the law I should remove the cover from the electrical connections in a boiler and check them, however some covers on boilers are gas sealed, and should only be removed by some one registered as gas safe, one has to assume if the cover which needs to be removed to check electrical connections is sealed it will be clearly marked as so, however I am told this is not always the case, so the electrician could cause danger in his attempts to remove it, so what ever the law says, he really has to carry on as before and leave the boiler where it is gas powered for the gas safe guy.
In other words do the EICR as instructed when taking the C&G 2391 exam, and take no notice to what the new law says. BS7671:2018 as with every other edition before it gives a date after which designs must follow it, and once we reach that statement we should stop reading if designed before that date, and select the edition in force at the time of design, however this would mean carrying all editions and amendments of the wiring regulations, which we clearly can't do, so in real terms we may give reference to wiring regulations to support what we say, but we are not actually seeing if the installation complies with regulations, we are looking for dangerous and potentially dangerous items.
@plugwash has given the link, and I would say most use that as a guide, even then some will not agree with what it says, to my mind the inadequate provision for socket-outlets is not really a reason to fail an installation, as that could be rather temporary and not exist 10 minutes after the inspection.
Personally where the premises are used by more than the owner and his family, so the users of the premises may not be of a mental state to under stand dangers be it children or others may use the premises, then the installation should be designed with that in mind, it is all well and good for me to say neither me or my wife will be in danger as we are not daft enough to play with electrics or go around drilling walls etc, but when my son was 14 years old he passed his RAE exam and it was clear to me he would play electrics, so I wanted to protect him, so I installed RCD protection,
however if the property had been rented that option would not have been open to me, only the landlord could have fitted the RCD's, they were not required in the early 90's when they were fitted, but I felt there was a potentially dangerous situation in that my son may play with 230 volt, so I fitted RCD protection.
So we return to the phrase "potentially dangerous" and I felt back in 1990's it was potentially dangerous, so how can I hand on heart say today RCD protection is not required. However when moving in here, it took 4 months before I had a all RCBO board fitted, the 28 days allowed is not really long enough to get some potentially dangerous items corrected, I have still not replaced the steps around the outside of my house, which can get moss on them, or snow, and also be potentially dangerous, does it really matter if the danger is slippery steps, non child proof gate, or rickety garden shed, in most situations we assess the risk, and decide if it needs improving and when, with my garden steps I can use the set other side of house with a hand rail, so feel not urgent to correct, that is my personal opinion, the same as the EICR is the inspectors personal opinion, and it does not really matter if he does not highlight some potentially dangerous items or if he highlights potentially dangerous items which most would accept, it has his personal opinion.