Ok, all boilers seem to have faults that are particular to that boiler. Anyone found any short cut tests or simple fixes?
I'll go first
Vokera Flowmatic/Excell range.
Problem: dhw runs hot for a short while and then cold for ages before firing up.
Probable cause: restricted diff air press venturi causing gas flame to drop out when a call to modulate down is active
Quick test: remove two bottom corner screws from the combustion case cover and slightly wedge open with the blade of a screwdriver. The change in diff air press will cause the boiler to modulate normally.
No need for too much stripping down or test equipment.