Morning everyone,
I'd like to get some second opinions if possible please. As some of you will know, I'm a qualified electrician/electrical engineer but am not registered with a scheme as I'm employed in industry. From time to time I do notifiable work and non notifiable (and indeed do notify when required), but in some cases when time doesn't permit, I bring in a registered domestic Sparks to do the work for me to save me the hassle.
I'm currently trying to have my shower cable and RCD shower unit replaced which is a time consuming job due to the length and route of the cable - so this is one of those times I've asked somebody in to quote. 2 electricians have been so far and both have said they will need to upgrade/change the main equipotential bonding arrangements at the house as they're not satisfactory as they stand. I'm arguing this fact as I believe them to be satisfactory.
The stated reasons for MEB being no good:
1) Water pipe is not bonded within 600mm of point of entry to the house.
2) central heating pipework below boiler not bonded to main earth terminal and not cross bonded to each other.
Last year we had to have a new water pipe as the original one kept rotting through under the front garden. The new water pipe was fitted by Severn Trent contractors free of charge (long story). Ultimately however, the new pipe had to take an entirely different route from the street to the house and a new entry point and stop cock was fitted by them. The new entry point is on the other side of the house to the original and a very good distance from the consumer unit location in the garage. To bond the new pipe within 600mm of entry would have meant installation of around 30 metres of 10mm earth cable and either pulling up much of the upstairs flooring or drilling through walls and mounting the cable on the interior walls of the house etc. Therefore I considered this to be totally not "practicable".
The gas meter for the property remains in its original location in a cupboard off the kitchen and this is bonded with 10mm cable and is accessible at all times. The new water pipe passes through this cupboard on its way to upstairs. Therefore, I extended the bonding from the clamp on the gas meter pipework to the new water pipe. This bonding location is around 4 metres from the entry of the pipe into the house. I considered that this was the most practicable and reasonable solution to get the MEB done.
As for the CH pipes, it's my understanding of the regs that unless the CH pipes can be classed as "extraneous conductive parts" (due to travelling underground etc) then they don't require bonding. I have always cringed at seeing plumbers and sparks cross bonding every single pipe to and from a boiler when it's completely not necessary to do it. The CH pipework is showing me a 0.1 ohms reading between the boilers electrical supply CPC as it's all earthed through the boiler as you would expect.
So in my mind, these two sparks are using the regulations surrounding bonding incorrectly. Does anybody concur?
I'd like to get some second opinions if possible please. As some of you will know, I'm a qualified electrician/electrical engineer but am not registered with a scheme as I'm employed in industry. From time to time I do notifiable work and non notifiable (and indeed do notify when required), but in some cases when time doesn't permit, I bring in a registered domestic Sparks to do the work for me to save me the hassle.
I'm currently trying to have my shower cable and RCD shower unit replaced which is a time consuming job due to the length and route of the cable - so this is one of those times I've asked somebody in to quote. 2 electricians have been so far and both have said they will need to upgrade/change the main equipotential bonding arrangements at the house as they're not satisfactory as they stand. I'm arguing this fact as I believe them to be satisfactory.
The stated reasons for MEB being no good:
1) Water pipe is not bonded within 600mm of point of entry to the house.
2) central heating pipework below boiler not bonded to main earth terminal and not cross bonded to each other.
Last year we had to have a new water pipe as the original one kept rotting through under the front garden. The new water pipe was fitted by Severn Trent contractors free of charge (long story). Ultimately however, the new pipe had to take an entirely different route from the street to the house and a new entry point and stop cock was fitted by them. The new entry point is on the other side of the house to the original and a very good distance from the consumer unit location in the garage. To bond the new pipe within 600mm of entry would have meant installation of around 30 metres of 10mm earth cable and either pulling up much of the upstairs flooring or drilling through walls and mounting the cable on the interior walls of the house etc. Therefore I considered this to be totally not "practicable".
The gas meter for the property remains in its original location in a cupboard off the kitchen and this is bonded with 10mm cable and is accessible at all times. The new water pipe passes through this cupboard on its way to upstairs. Therefore, I extended the bonding from the clamp on the gas meter pipework to the new water pipe. This bonding location is around 4 metres from the entry of the pipe into the house. I considered that this was the most practicable and reasonable solution to get the MEB done.
As for the CH pipes, it's my understanding of the regs that unless the CH pipes can be classed as "extraneous conductive parts" (due to travelling underground etc) then they don't require bonding. I have always cringed at seeing plumbers and sparks cross bonding every single pipe to and from a boiler when it's completely not necessary to do it. The CH pipework is showing me a 0.1 ohms reading between the boilers electrical supply CPC as it's all earthed through the boiler as you would expect.
So in my mind, these two sparks are using the regulations surrounding bonding incorrectly. Does anybody concur?