hi i got a hob rated at 6600W. A microwave rated at 3600W and a single oven rated at 3600W
Now the micro and the oven manufacturer say that they must not
be fused at 13A or put on a plug.
I think to do with the cleaning cycle which runs at pretty much
full power for 2 hours. Therefore no diversity allowed
Can i run them on 2.5mm radials with 16A mcb to their own cooker switch?
The hob i assume is allowed diversity which i have worked out to be roughly 16 A too.
Now do i put that on 16A mcb or do i disregard the diversity and
assume full load which is about 28A?