Last night I was alarmed to find water dripping out of my loft hatch! Turns out the CH expansion tank was overflowing (the overflow pipe to the outside world must have had an airlock or something because when I tapped it a few times it started to work again and the water ran off).
Its a conventional boiler with HWC, cold storage tank and smaller CH expansion tank.
The Ballcock Valve in the expansion tank is working fine and cuts off when there is about 2 inches in the bottom of the tank. There is a further 6 inches (about 10 litres worth) of room to expand before the level would reach the overflow. Does this leave the Boiler Vent as the culprit? How would I remedy this situation?
Another issue that I discovered whilst up there, is that in the Cold Storage tank, the HWC vent outlet is beneath the water level by an inch? Is that correct?
I guess the first thing is to redesign the overflow pipework to prevent airlocks in the future, but then what?
All help appreciated, I really don't fancy a wet floor again!
Its a conventional boiler with HWC, cold storage tank and smaller CH expansion tank.
The Ballcock Valve in the expansion tank is working fine and cuts off when there is about 2 inches in the bottom of the tank. There is a further 6 inches (about 10 litres worth) of room to expand before the level would reach the overflow. Does this leave the Boiler Vent as the culprit? How would I remedy this situation?
Another issue that I discovered whilst up there, is that in the Cold Storage tank, the HWC vent outlet is beneath the water level by an inch? Is that correct?
I guess the first thing is to redesign the overflow pipework to prevent airlocks in the future, but then what?
All help appreciated, I really don't fancy a wet floor again!