Got called by my neighbours tonight as their RCD kept tripping when they turn on high power loads. They had a spark round last week who couldn't find the problem (said it was probably something they had plugged in which had the fault)
After trying to find out what they had plugged in and not getting very far I went through each circuit in turn with a simple continuity test, narrowed it down to neutral-earth fault with a bit of cable between 2 sockets.
As I haven't fully read up on part P / what is notifyable - can I replace a bit of 2.5mm t&e between two sockets on a ring, or is this something thats notifyable ?
As a separate thing - while I was there I noticed the Neutral sat at around 40v to Earth, as they were off out for the night I didn't get a chance to do much other testing on this, although the one quick test I did is that its still 40v with the RCD and isolator off (tested supply side, load side the neutral drops to 0v).
Supply is TT, main earth cable from rod comes in from rod to CU earth block, along with bonds from various pipes.
As people don't get a shock off things that are earthed - could this be a supply neutral problem ? or is there something I've missed ?
Got called by my neighbours tonight as their RCD kept tripping when they turn on high power loads. They had a spark round last week who couldn't find the problem (said it was probably something they had plugged in which had the fault)
After trying to find out what they had plugged in and not getting very far I went through each circuit in turn with a simple continuity test, narrowed it down to neutral-earth fault with a bit of cable between 2 sockets.
As I haven't fully read up on part P / what is notifyable - can I replace a bit of 2.5mm t&e between two sockets on a ring, or is this something thats notifyable ?
As a separate thing - while I was there I noticed the Neutral sat at around 40v to Earth, as they were off out for the night I didn't get a chance to do much other testing on this, although the one quick test I did is that its still 40v with the RCD and isolator off (tested supply side, load side the neutral drops to 0v).
Supply is TT, main earth cable from rod comes in from rod to CU earth block, along with bonds from various pipes.
As people don't get a shock off things that are earthed - could this be a supply neutral problem ? or is there something I've missed ?