Hi,
I have a Potterton 24 that’s running warm and cold water only.
The CH works ok but when I run the hot water, the burner light ignites and then goes off after about 45 secs, the water then runs from warm to cold and this continues for however long the hot water tap/shower is on. It doesn't get hot at all. I've also noticed that the pressure has risen to about 3.5 when the hot water is turned on from a tap/shower.
Does anyone know what could be causing this please?
I read in a previous post that it may be the Boiler Diverter valve Diaphragm, does that sound likely to anyone else and would that be easy to replace if its that?
Thanks for helping out,
Andy.
I have a Potterton 24 that’s running warm and cold water only.
The CH works ok but when I run the hot water, the burner light ignites and then goes off after about 45 secs, the water then runs from warm to cold and this continues for however long the hot water tap/shower is on. It doesn't get hot at all. I've also noticed that the pressure has risen to about 3.5 when the hot water is turned on from a tap/shower.