This is job I went to about two years ago. I issued an "AT RISK" warning about these lights. THe trannies are buried in fibreglass & the fittings are surrounded by unfixed standard pvc soil pipe. Went back today & the client told me they had had an "electrician" round and he had said they were fine.
In any case, her house was newbuild & the NHBC would not issue a cert nor Zurich underwrite her guarantee if it were wrong, would they?
The other defects noted here were single PEB conductor to gas & water, broken at all three clamps.
And two CU's without single point of isolation or warning sticker. Doesn't bode well for new build really.
The second piccy was a call-out to a "non-tripping RCD". Anyone work out why?