Here's some observations from a PIR report on a recent house survey given to me, form the new owner. There were 19 in all, I've picked the best one's out. (I've been on DIYnot before but cant log on under my old user name for some reason) - vera & co
The PIR report was on a green NIC paper, I did not see any other pages.
This is it verbatim:
3, no main earth from supply company. Code 3 + 1
8, no earth onto metal socket boxes. Code 4
9, no round 20mm gromits on entry holes to socket boxes and light switch boxes. Code 4
12, no main earth onto central heating pipe work. Code 1
14 no suplementery cross bonding bathroom pipe work or radiator. Code 4
15 no mains powerd smoke detectors. Code 1
17 no RCD protection on lighting circuits as specified 17th edition regs BS July 08. Code 1
18 high earth reading. Code 1
My observation's;
3 the property is supplied from next door and there is no evidence of there ever been a main earth.
9 the light switch patteress are the 16mm type with the bevelled/rounded entry holes.
14 not required, no shower etc just lighting circuit.
15 there was 1 cheap battery powered smoke detector.
18 no main earth so no Ze reading!
I've only done a quick visual on the installation and will be going back next week to rectify.
have no idea who the 'Electrician' was!
The PIR report was on a green NIC paper, I did not see any other pages.
This is it verbatim:
3, no main earth from supply company. Code 3 + 1
8, no earth onto metal socket boxes. Code 4
9, no round 20mm gromits on entry holes to socket boxes and light switch boxes. Code 4
12, no main earth onto central heating pipe work. Code 1
14 no suplementery cross bonding bathroom pipe work or radiator. Code 4
15 no mains powerd smoke detectors. Code 1
17 no RCD protection on lighting circuits as specified 17th edition regs BS July 08. Code 1
18 high earth reading. Code 1
My observation's;
3 the property is supplied from next door and there is no evidence of there ever been a main earth.
9 the light switch patteress are the 16mm type with the bevelled/rounded entry holes.
14 not required, no shower etc just lighting circuit.
15 there was 1 cheap battery powered smoke detector.
18 no main earth so no Ze reading!
I've only done a quick visual on the installation and will be going back next week to rectify.
have no idea who the 'Electrician' was!