Plastic light switches in plastic patress -what do I do with

Joined
8 May 2009
Messages
36
Reaction score
0
Location
Newcastle upon Tyne
Country
United Kingdom
Ive got some new platerboard walls with dry lining patress boxes and standard white plastic switches (we've batten out the walls to hide pipes) the T&E comes to the switch as normal but no where is there at tag or connecting for the earth core -what should I do with it? Cut it back, tape it up, stick it in some choc block or disconnect the far end??
 
Sponsored Links
Leave it the same length as the other conductors, sleeve it and put it in a piece of connector block.

You should not consider any of your other suggestions
 
And you might find out how very dodgy the last option is if you ever drilled into a cable with no earth core in it...
 
Sponsored Links
The CPC isn't there to protect the cable against being drilled, screwed etc.
Had one where someone had put a 5" screw through a 3" door frame and managed to go put it through the space between the two adjacent live cores in 3c&e so the 2 way lighting ckt wouldn't switch off normally.
And it was in a safe zone ;)
 