Please help with my Honeywell CM927 dilemma!

Joined
28 Nov 2009
Messages
7
Reaction score
0
Location
Northamptonshire
Country
United Kingdom
I replaced my old Honeywell thermostat with a new CM927 today but... it doesnt work... Power light is on - remote thermostat turns unit on at right temperature, but boiler doesnt fire up... I have reinstalled the old thermostat in case I had blown a fuse somewhere but that works perfectly.

Wiring on old unit goes 1 to 5

and wires go into 1 = Permanent live 2= neutral 3= switched live.

There are four wires going into the unit - two live and two neutral

The new unit has six slots N L L A B C

I wired 1 into L, the 2 neutrals into N and the switched live into B....

So why isnt it working?
 
Sponsored Links
cause you havent wired it correctly

your new receiver has a permanent live to L

a permanent neutral to N

and your switched live and live return go in A and B
 
Ok - sussed it !

Had to put a bridging wire from second L connector to A - B is correct as switched live = all works now....
 
Sponsored Links
To keep it as simple as possible, A also has to be connected to Permanent Live and then B will become Switched Live.

Edit:You just beat me to it. :)
 