Hello guys.
To accomodate a new 16amp / 3.5Kw oven, I have laid a 6mm T/E from my consumer unit to a new 45amp cooker switch, going onto a CCU.
There is a spare 16A MCB in the consumer unit but my calculations tell me I need a higher rated (19) MCB.
I = 3500 / (230*0.8) = 19.02
Can some confirm this is indeed the right way to calculate the rating for the MCB?
Notes
Only the oven connects to the CCU, no other appliances
I will be using a gas hob
I have connected the oven to the CCU with 2.5mm T/E heat resistant