Most straightforward way to measure pressure generated by gravity (your present hot-water system) is, every metre above the draw-of point (shower head on the riser rail - most likely) generates 0.1bar. i.e 10m difference in height = 1.0 bar.
So, likely maximum pressure (static - when water is still) would be 0.2-0.3 bar in a bungalow.
AND, DO NOT mix mains pressure coldwater and tankfed hot-water in a bath/shower mixer. the cold water will push any hot flow back towards the storage vessel. Even (double)check/one-way valves (as required by water regs) would be problematic as it would further restrict hot flow through them to the bath/shower mixer.
So, I would suggest either, a) (cheapest) tank fed cold water - at same pressure as hot, & a shower pump to boost filling/flowrates - you may need to enlarge both capacities of hot-water storage vessel/domestic storage cistern in roofspace to minimise water starvation.
b) dearer, a mains pressure unvented cylinder with balanced hot&cold pressures
c) possibly dearer yet, a 'combination' boiler oil/gas to provide effectivley mains pressure instantanious hot water provision.
d) (not very likely) bury the bath so deep in the floor you get 0.5bar pressure.