Hi All,
I'm after a some advice please on a job I recently carried out for a own peace of mind.
I was asked to fit a new dual rcd consumer unit to a property with a PME incoming supply. Before I changed the board I carried out an earth loop impedance test and measured 0.1 ohms which I was happy with. I fitted the board but when I tried to do an rcd test my megger meter didnt like it. I then placed a short between earth and neutral to simulate a fault and the rcd still didn''t trip. At this point I thought the rcd's may be faulty and replaced them. They still didn't trip. I also noticed that I could feel a small current across a socket and a light switch as I turned them on. This set the alarm bells ringing as there seemed to be no earth. I proved this by installing an earth stake and connecting it directly to the consumer unit. I then tested the RCD's and they functioned correctly.
My main questions are:
Why would the customer not have noticed this small current before I changed the board?
How can my tester give me an original Ze of 0.1 ohms with no earth? is it because the earth and neutral are the same potential?
With the leakage current I could feel at the switch and socket, should it not have tripped the Rcd when I installed the earth stake?. They were no longer present after this.
Lastly, after I spoke to somebody from EDF who were not the most helpful, I installed a new earth link between the head and cu. Can you tell me if this is entirely necessay.
If anyone can help me understand this I would really appreciate it as this is the first time I have encountered these problems with a PME system.
Thanks
Coys2006
I'm after a some advice please on a job I recently carried out for a own peace of mind.
I was asked to fit a new dual rcd consumer unit to a property with a PME incoming supply. Before I changed the board I carried out an earth loop impedance test and measured 0.1 ohms which I was happy with. I fitted the board but when I tried to do an rcd test my megger meter didnt like it. I then placed a short between earth and neutral to simulate a fault and the rcd still didn''t trip. At this point I thought the rcd's may be faulty and replaced them. They still didn't trip. I also noticed that I could feel a small current across a socket and a light switch as I turned them on. This set the alarm bells ringing as there seemed to be no earth. I proved this by installing an earth stake and connecting it directly to the consumer unit. I then tested the RCD's and they functioned correctly.
My main questions are:
Why would the customer not have noticed this small current before I changed the board?
How can my tester give me an original Ze of 0.1 ohms with no earth? is it because the earth and neutral are the same potential?
With the leakage current I could feel at the switch and socket, should it not have tripped the Rcd when I installed the earth stake?. They were no longer present after this.
Lastly, after I spoke to somebody from EDF who were not the most helpful, I installed a new earth link between the head and cu. Can you tell me if this is entirely necessay.
If anyone can help me understand this I would really appreciate it as this is the first time I have encountered these problems with a PME system.
Thanks
Coys2006