HISTORY:
Gas Engineer visits property: Polarity on boiler reversed.
Electrician visits: Polarity OK.
Gas Engineer visits: Polarity reversed.
Electrician visits: Polarity reversed. Calls DNO. DNO arrive, test, and Polarity OK.
HOW??
TT system with no rod, but evidence of tampering to cut-out & link to cutout. for earthing. Zs of 12.16 - earth connection coming from pipework. Ze 87.4.