looked at this boiler today, not been working for over a month, customer has had numberous engineers out to look at it.
i've no idea what they did, but it hasn't fixed it, probably made it worse.
240v at SWL but no permanate live at L.
240v into the resetable lock out, but no wire coming off of that onto the PCB. random! checking the manual didn't help because it showed a brown wire going to the PCB. this 1 had a blue wire heading for the neutral.
i but the gas valve plug into the 'test' point and it now had 240v at the blue wire going to the PCB. checked the voltage going to APS, 120v (+ - 10%) also all the other connects, all approx 120v.
very odd i thought.
anyways, i was only there to look over and to investigate 'if' a new PCB had been installed, apparently the previous company had charged for 1, the owner of house had seen the exchange the PCB. it was certainly NOT a new PCB and my thoughts NOT the correct PCB.
long post i know, but any of you more experienced guys care to comment?
thanks, Tim.
i've no idea what they did, but it hasn't fixed it, probably made it worse.
240v at SWL but no permanate live at L.
240v into the resetable lock out, but no wire coming off of that onto the PCB. random! checking the manual didn't help because it showed a brown wire going to the PCB. this 1 had a blue wire heading for the neutral.
i but the gas valve plug into the 'test' point and it now had 240v at the blue wire going to the PCB. checked the voltage going to APS, 120v (+ - 10%) also all the other connects, all approx 120v.
very odd i thought.
anyways, i was only there to look over and to investigate 'if' a new PCB had been installed, apparently the previous company had charged for 1, the owner of house had seen the exchange the PCB. it was certainly NOT a new PCB and my thoughts NOT the correct PCB.
long post i know, but any of you more experienced guys care to comment?
thanks, Tim.