Hi and thanks for for quick response..The fused mains switch is a 3 amp ...It works just as you'd expect it to, right up to the point where it should ignite and the green light goes on and on the ignition click the 2A blows...The fan sounds as if it works ok.gasandoilman said:what size fuse have you got on your fused switch?
Could it be the fan? at what point does it blow
If you want to make some money I suppose.£160 !!!
Well I disconected the Gas Valve Solenoid..But it blew the fuse again...I've read somewhere on the Forum that a suppressor capacitor on the Spark Generator could cause this but I'm not sure if it was the same model boiler they were talking about.ChrisR said:Dave of course you're right - I read "as the Domestic supply is turned on" and shot past Timbuck's second post!
Presumably it does it on CH too??
(goes off to see what's on that other board - the "full sequence" one...)
Yep I concur - try disconnecting the connectors on the gas valve (not the board end plug or you'll be disconnecting the overheat stat which would stop things working).
If the fuse doesn't blow, but it goes on to the ignition sparks, you've found it.
Brilliant deduction it was the pump...Hoooray. I didn't check it before cos iwas only using it for domestic supply......It's a Myson Compact CP61..What is the best replacement part if I cant find one like it....And question can I still us the domestic supply with the pump disconnected?.poxi said:Disconnect wiring on pump and try.