potterton boiler problem

Joined
22 Dec 2008
Messages
14
Reaction score
0
Location
Humberside
Country
United Kingdom
need help please low system pressure light is on pressure gauge reads 1.5 bar have bleed the radiators small amount of air came out .. but still light on and no hot water or heating .. help please as my kids now resemble eskimo s
 
Sponsored Links
I'm gonna go for a potterton puma or an Ideal Response :LOL:
blocked Low Water Pressure Switch.
 
some, if not a lot, more info would be handy. crystal ball readings cost extra
 
Sponsored Links
I'm gonna go for a potterton puma or an Ideal Response :LOL:
blocked Low Water Pressure Switch.

silly me, just see you said potterton. Well anyway, It was still a fine guess :)

Blocked Low Water Pressure Switch

Round thing with 3 wires on it. Drain system, unscrew it, clean it out as best as possible. Any further probs, replace it.
Temp naughty fix, swap wires over :eek: ;)
 
I'm gonna go for a potterton puma or an Ideal Response :LOL:
blocked Low Water Pressure Switch.

silly me, just see you said potterton. Well anyway, It was still a fine guess :)

Blocked Low Water Pressure Switch

Round thing with 3 wires on it. Drain system, unscrew it, clean it out as best as possible. Any further probs, replace it.
Temp naughty fix, swap wires over :eek: ;)
is that the water flow switch with micro switch on if so you reckon it's off the shelf part or ordered if it needs it
 
ignore last thanks mickyg
found it only got 2 wires and they were tucked round the back of it thanks for your help will go to plumb centre and get one just in case
 