We have a combi 80 which has a persistant occasional lockout problem.
It started about a month ago when it started locking out on the HW side, this was traced to a sticky flowswitch which I've replaced together with the microswitch, (and the auto vent as that was leaking) that improved things on the HW side but I was still getting an occasional lockout when the CH was hot together with a lot of clicking on the main board.
That was a faulty relay so I replaced the main board, clicking fixed, less frequent lockouts
Now I still get an occasional lockout on the CH side accompanied by banging in the pipes and water from the vent, this occurs maybe once every 4 or 5 days although the banging pipes seems to occurs at pretty much the same time every day, late at night when the heating has been on for a few hours and sometimes after running a shower/bath in the morning.
I'm assuming there is some kind of overheat going on when the CH turns off so I've replaced the CH stat as it measured just below spec, no change.
The pump and fan seems to run fine and carries on running for a while when the heating goes off, the other two HW stat's measure within specs, diverter was only replaced about 2 months ago no heating of the CH pipes when HW is on, CH expansion vessel is up to pressure.
I'm at a a bit of a loss where to go from here as following the fault finding chart shows normal function, I've sat and watched the boiler when it turns off (that was fun) and the flame seems to stop right away.
Only thing I can think of is that the pump although working is running slow maybe and not dissipating all the heat when the CH is really hot? (it was replaced during a BG service last year)
Any thoughts? Engineer coming in the next couple of weeks for a service but wife and kids away next week so would be a good opportunity to sort it if I can.
Thanks!
It started about a month ago when it started locking out on the HW side, this was traced to a sticky flowswitch which I've replaced together with the microswitch, (and the auto vent as that was leaking) that improved things on the HW side but I was still getting an occasional lockout when the CH was hot together with a lot of clicking on the main board.
That was a faulty relay so I replaced the main board, clicking fixed, less frequent lockouts
Now I still get an occasional lockout on the CH side accompanied by banging in the pipes and water from the vent, this occurs maybe once every 4 or 5 days although the banging pipes seems to occurs at pretty much the same time every day, late at night when the heating has been on for a few hours and sometimes after running a shower/bath in the morning.
I'm assuming there is some kind of overheat going on when the CH turns off so I've replaced the CH stat as it measured just below spec, no change.
The pump and fan seems to run fine and carries on running for a while when the heating goes off, the other two HW stat's measure within specs, diverter was only replaced about 2 months ago no heating of the CH pipes when HW is on, CH expansion vessel is up to pressure.
I'm at a a bit of a loss where to go from here as following the fault finding chart shows normal function, I've sat and watched the boiler when it turns off (that was fun) and the flame seems to stop right away.
Only thing I can think of is that the pump although working is running slow maybe and not dissipating all the heat when the CH is really hot? (it was replaced during a BG service last year)
Any thoughts? Engineer coming in the next couple of weeks for a service but wife and kids away next week so would be a good opportunity to sort it if I can.