Hi,
Having problem with potterton Kingfisher 2 RS 60 (G/c 41 607 19),. The pilot goes out intermittently.
Have serviced boiler (badly needed service), checked gas rate. Heat exchanger cleaned. Seals checked. thermocouple changed as a matter of course (old thermocouple was ok drop out time 25S).
Burning a lot better after service (stripped and cleaned burner assy). However the customer says pilot still goes out occasionally. No sign of vitiation or flame lift.
Could the gas valve be faulty or is there anything else I should check. (The overheat stat is not wired in series with the thermocouple). Also on some of these type of boilers I find the flames do not burn as blue as on the fan flue type appliances (even after a good service0, any comments.
Kind regards
Harry (RGI)