I have a Potterton Netaheat 10/16 Mk II (gas) boiler which has recently failed to fire up
The boiler gets part way through its start up sequence, but the main burners never fire up
The boiler has been operating normally and there have been no recent changes
The room and / or cylinder thermostats call for heat, the motorised valves open and the pump starts
The relevant control should then then instruct the boiler to start up
Some time ago, I found a description of the start up sequence for this boiler
I thought it was on this forum, but I can no longer see it - fortunately, I made a hard copy
I think I have been able to identify where in the start up sequence the boiler fails
However, it would be useful for some advice to confirm what I think is at fault
The start up sequence I found for a normally operating Netaheat boiler is summarised as follows:
1) thermostat calls for heat, supplying power to the electronics
2) the fan starts
3) a pressure switch detects that air is flowing through the boiler
4) ignition is delayed for a "purge period"
5) the pilot valve is opened and the spark generator is activated
6) the pilot ignites and is detected by the ignition electrodes
7) spark generator is de-activated, the main valve is opened and the main burner is ignited by the pilot flame
For my boiler, the sequence gets as far as the pilot being lit, but the main burners never light
The Potterton documentation for the boiler shows two solenoids in the gas valve
From the symptoms, it seems to me that the main gas valve solenoid has failed
I am reasonably competent with the electrics and have measured the voltages supplied to the gas valve from the PCB
After the pilot is lit, both BR and R terminals on the PCB measure about 230V AC wrt the B (neutral) terminal
With all power isolated, I then measured across the gas valve solenoid coils:
a) the BR coil measured about 2.7kohms - the documentation shows a resistor in series with one of the gas valve solenoids
b) the R solenoid appeared to be totally open circuit and I correlate this to the failure of the main gas valve
Does this sound like the most likely cause ?
Is there anything else I can check or do to get my boiler working
I've read various threads on here in relation to old Potterton boilers
Opinion seems to be divided about whether to repair the old one or get a more efficient new boiler
As I am recovering from Xmas overspend, the plan is to repair the existing boiler / keep it going a few more years
The boiler was fitted in 1984 and has been regularly serviced - most recent service was July 2007
About 4 years ago the PCB and relay were changed
At the same time I purchased a spare relay - I tried changing the relay, but the boiler still does not start
I did not expect it to as I think it is the main solenoid on the gas valve that has failed
I have checked the fuse on the PCB and this is OK
Thanks for any advice and help
The boiler gets part way through its start up sequence, but the main burners never fire up
The boiler has been operating normally and there have been no recent changes
The room and / or cylinder thermostats call for heat, the motorised valves open and the pump starts
The relevant control should then then instruct the boiler to start up
Some time ago, I found a description of the start up sequence for this boiler
I thought it was on this forum, but I can no longer see it - fortunately, I made a hard copy
I think I have been able to identify where in the start up sequence the boiler fails
However, it would be useful for some advice to confirm what I think is at fault
The start up sequence I found for a normally operating Netaheat boiler is summarised as follows:
1) thermostat calls for heat, supplying power to the electronics
2) the fan starts
3) a pressure switch detects that air is flowing through the boiler
4) ignition is delayed for a "purge period"
5) the pilot valve is opened and the spark generator is activated
6) the pilot ignites and is detected by the ignition electrodes
7) spark generator is de-activated, the main valve is opened and the main burner is ignited by the pilot flame
For my boiler, the sequence gets as far as the pilot being lit, but the main burners never light
The Potterton documentation for the boiler shows two solenoids in the gas valve
From the symptoms, it seems to me that the main gas valve solenoid has failed
I am reasonably competent with the electrics and have measured the voltages supplied to the gas valve from the PCB
After the pilot is lit, both BR and R terminals on the PCB measure about 230V AC wrt the B (neutral) terminal
With all power isolated, I then measured across the gas valve solenoid coils:
a) the BR coil measured about 2.7kohms - the documentation shows a resistor in series with one of the gas valve solenoids
b) the R solenoid appeared to be totally open circuit and I correlate this to the failure of the main gas valve
Does this sound like the most likely cause ?
Is there anything else I can check or do to get my boiler working
I've read various threads on here in relation to old Potterton boilers
Opinion seems to be divided about whether to repair the old one or get a more efficient new boiler
As I am recovering from Xmas overspend, the plan is to repair the existing boiler / keep it going a few more years
The boiler was fitted in 1984 and has been regularly serviced - most recent service was July 2007
About 4 years ago the PCB and relay were changed
At the same time I purchased a spare relay - I tried changing the relay, but the boiler still does not start
I did not expect it to as I think it is the main solenoid on the gas valve that has failed
I have checked the fuse on the PCB and this is OK
Thanks for any advice and help