My Potterton Netaheat 6/10E (CG No. 4160168) has for a few months now suffered from an intermittent fault that is becoming increasingly more frequent. I have followed the operational flow chart in the manual and the fan switches on ok, the ignition sparks ok, the pilot light lights ok, and usually the main burner fires ok, but sometimes accompanied by what sounds like a very noisy sticking oscillating valve the main burner goes out (but not always). Often coming on seconds later with more noisy valve sounds. A thump to the base of the boiler casing often works. I've checked the voltage to the solenoid valves: terminals T1 to T3 GV1 main burner is 240 vac which is correct; terminals T2 to T3 GV2 pilot is 172 vac (should be 240 vac). But I don't have problems with the pilot only the main burner which looks like it's getting the correct volts. Does this mean I've got two problems gas valve and the electronics board and the fans getting noisy too. All these parts could add up to £300 to £400 plus vat plus fitting. The boilers ~ 20 years old and hasn't had any new parts in at least 10 years. I would seriously think about a new boiler and according to the 'guide to the condensing boiler installation assessment procedure for dwellings' this will have to be a condensing one, but there do seem to be many restrictions on condensing flue positions e.g. 2.5 m from boundary, not over footpath or patio, not visible from front of building etc. are these all compulsory? If so it means I will have to re-site a new boiler which will not only be expensive but very disruptive re-routing gas and water pipes, and ending up with the boiler in a non-ideal position. To avoid this I would like to get my current boiler working correctly.