Hi, looking for some advice please.
I have a Prima 80F boiler which has the following fault:
1. Call for Heat
2. Small click heard followed by start of Fan
3. Approx 1 second later, larger click heard followed by fan stopping
4. Boiler retrys again after approx 4 to 5 seconds
5. 1 in 5 attempts results in the boiler igniting correctly
I had a similar problem about 4 years ago which was the PCB Control Unit, but on that occasion, the boiler failed to light completely. The fact that it now occasionally lights made me suspect the Pressure Switch, which I have now replaced, but the fault is still present.
Is it possible for the Control Unit to fault intermittently like this? If not, any other likely cause?
I have checked the obvious, such as connectors etc. I have also checked that there is 240V to the common of the Pressure Switch, which there is.
Any advise much appreciated before I spend over £100 on a new PCB.
Many thanks in advance
I have a Prima 80F boiler which has the following fault:
1. Call for Heat
2. Small click heard followed by start of Fan
3. Approx 1 second later, larger click heard followed by fan stopping
4. Boiler retrys again after approx 4 to 5 seconds
5. 1 in 5 attempts results in the boiler igniting correctly
I had a similar problem about 4 years ago which was the PCB Control Unit, but on that occasion, the boiler failed to light completely. The fact that it now occasionally lights made me suspect the Pressure Switch, which I have now replaced, but the fault is still present.
Is it possible for the Control Unit to fault intermittently like this? If not, any other likely cause?
I have checked the obvious, such as connectors etc. I have also checked that there is 240V to the common of the Pressure Switch, which there is.
Any advise much appreciated before I spend over £100 on a new PCB.
Many thanks in advance