potterton profile 60e

Joined
20 Jul 2008
Messages
1
Reaction score
0
Location
Surrey
Country
United Kingdom
i have a fault with a potterton profile 60e it fires up ok but after about 10-15 minutes the over heat stat pops out and the boiler casing gets quite hot. i suspected it was the boiler stat so i changed that along with the over heat stat, but the problem still persist. the flow and return are both getting hot any ideas
 
Sponsored Links
The Profile has a pump over-run thermostat. This may have failed so the pump is not working.

You don't say if you are fully pumped or have gravity HW. This affects the way the over-run works. It's all in the manual.

If you do not have the manual, you can find it on Baxi Partsarena
It is under Potterton - Boiler - Profile - 100E. This leads you to the installation manual for all Profile E Models.

You will have to install an activex program to view the manual.
 