thanks for all replies,the boiler was installed by heating company approx 3 yrs ago but were not prepared to service it when customer asked.
i was asked(oftec reg) to look at boiler when problem arose.i cleaned all baffles and heat exchanger it was really sooted up,i found that the heat exchanger fireproof lining on base had broken up,i contacted potterton who said that heatchanger now obsolete and so could not supply replacement,suggested repairing cracks with fire cement.
i then changed nozzle,checked and cleaned fuel filters and bled tiger loop pipes to pump,no debris in oil.(kerosene).checked pump pressure 105,
burner is riello 3 RDB1.air damper setting should be 2.4.
ran boiler fired up fine but still running rich set damper at 3.0 CO2 12.5%
but not consistant,but flue gas temp was way too high @ 240.
managed to get flue temp down to about 195.
about 3 weeks later it started to smoke badly again,so i changed pump and checked and cleaned nozzle,set up pressure but had to run to star with with damper wide open at 7.0 to stop smoke, i then gradually reduced to 3.5,no smoke but co2 at 5.5% and flue temp v.high again.flue gas analyser readings are very erratic,depending on length of run time.
it was suggested by another engineer poss cracked heat exchanger,would appreciate any ideas as i not come across this problem before