Hi All
This is a new post regarding a problem I have asked about before. We have a Powermax 155x Boiler supplying our heating and hot water at home and it has been suffering from pressure loss problems for a week or so now. What happens is that I re-fill the system to 1bar and then when the heating comes on the pressure rises to around 2.5bar. At this point the pressure relief valve vents some of the water to the outside. Consequently the pressure drops until it is at a safe level. This process repeats until the system cuts out due to lack of water... I then have to re-fill.... I think the system also has some trouble maintaining pressure when the heating/hot water is off...
My earlier post, which lead to identification of the expansion vessel as the possible problem, also got the reply:
It may be a duff expansion valve, if it's dripping at less than 3 bar.
The seat can get scored or they can get grit stuck in the valve If the latter, operating the red easing knob will open it and sometimes blow the grit out; usually a new valve is required.
Now I haven't got round to testing and replacing the expansion vessel yet but I don't know where/ can't find the expansion valve. Has anyone got any idea where this is? I also don't have a clue what the red easing knob is... any ideas?
I am also looking for a replacement expansion vessel. The one currently in place is a Zilmet 13B-001836 18 litre variety. Does anyone know where I can get a suitable replacement?
Any help would be gratefully appreciated.
Cheers
This is a new post regarding a problem I have asked about before. We have a Powermax 155x Boiler supplying our heating and hot water at home and it has been suffering from pressure loss problems for a week or so now. What happens is that I re-fill the system to 1bar and then when the heating comes on the pressure rises to around 2.5bar. At this point the pressure relief valve vents some of the water to the outside. Consequently the pressure drops until it is at a safe level. This process repeats until the system cuts out due to lack of water... I then have to re-fill.... I think the system also has some trouble maintaining pressure when the heating/hot water is off...
My earlier post, which lead to identification of the expansion vessel as the possible problem, also got the reply:
It may be a duff expansion valve, if it's dripping at less than 3 bar.
The seat can get scored or they can get grit stuck in the valve If the latter, operating the red easing knob will open it and sometimes blow the grit out; usually a new valve is required.
Now I haven't got round to testing and replacing the expansion vessel yet but I don't know where/ can't find the expansion valve. Has anyone got any idea where this is? I also don't have a clue what the red easing knob is... any ideas?
I am also looking for a replacement expansion vessel. The one currently in place is a Zilmet 13B-001836 18 litre variety. Does anyone know where I can get a suitable replacement?
Any help would be gratefully appreciated.
Cheers