Hi,
I have a 2 year old Viessmann Vitodens 050-W gas condensing boiler and a problem with keeping the pressure in the central heating system. When I pressurize the system to 1 bar and isolate the boiler the pressure holds so I assume there isn't a problem with the boiler itself.
When I pressurize the boiler to 1 bar and let it run normally with the heating on it takes around 1 hour to drop from 1 bar to 0. At the same time I lose around 170 ml in condensation and it takes me 30 sec. to fill the system up from 0 to 1 bar again.
Here is where I could do with some help from people who know far more than myself:
1) Am I on the right track thinking this clearly has nothing to do with the boiler itself and that I have a leak somewhere in the central heating system?
2) Given it only takes an hour to drop 1 bar and I need 30 sec for a refill am I correct in thinking the leak is fairly substantial? I am asking because if this is the case then it's fairly safe to assume it is somewhere under the floorboards on the ground floor - otherwise I would have seen water marks/damage somewhere
Thanks for your help,
Manuel
I have a 2 year old Viessmann Vitodens 050-W gas condensing boiler and a problem with keeping the pressure in the central heating system. When I pressurize the system to 1 bar and isolate the boiler the pressure holds so I assume there isn't a problem with the boiler itself.
When I pressurize the boiler to 1 bar and let it run normally with the heating on it takes around 1 hour to drop from 1 bar to 0. At the same time I lose around 170 ml in condensation and it takes me 30 sec. to fill the system up from 0 to 1 bar again.
Here is where I could do with some help from people who know far more than myself:
1) Am I on the right track thinking this clearly has nothing to do with the boiler itself and that I have a leak somewhere in the central heating system?
2) Given it only takes an hour to drop 1 bar and I need 30 sec for a refill am I correct in thinking the leak is fairly substantial? I am asking because if this is the case then it's fairly safe to assume it is somewhere under the floorboards on the ground floor - otherwise I would have seen water marks/damage somewhere