pressure vessel

Joined
9 Feb 2004
Messages
7
Reaction score
0
Country
United Kingdom
I have a eurocal 70/90 combi boiler. What air pressure should there be in my pressure vessel when the water pressure is 0 bar and the system is cold? The system supplies an average size 3 bedroom two storey house.
 
Sponsored Links
The air has to provid the equivalent head to the height of the system, so 0.5 bar will give 16ft, and 0.8 would be more than adequate. Your boiler should work on both, but understand some boilers seem to need a bit more. Your instruction manual should tell you.

The water pressure should be set to 0.2 bar above the air pressure.
 
Thanks Oilman.
I will check the pressure next time the boiler trips out.
Chris
 
Sponsored Links
Charged the pressure vessell with a footpump to 0.8 bar and tightened up a compression joint to stop a minor leak - Everything now works fine, and the water pressure in the system has remained steady for two days now.

Thanks for your advice.
 