pressurising old gravity heating system queery

Joined
27 Apr 2010
Messages
27
Reaction score
2
Country
United Kingdom
Hi all i am fitting a new oil condensing boiler out in the garage, adding a megaflow and doing away with the f & e tank and water storage tank, the megaflow will be in mid house. The question is, can i fit the pressure vessel and quick fill loop in the new "airing cupboard" and have it connecting into the heating at the coil where it enters the cylinder? or is there anywhere specific on the heating pipework that the fill loop should go? The vessel and pressure reducing set up for the megaflow will be in there too so i could Tee off the mains running to it to feed the heating sides vessel as the new boilers site in the garage has no mains supply. Thanks in advance for any comments
 
Sponsored Links
safety valve on or near boiler , filling loop were ever, generally on return , pressure gauge will be required near filling loop providing visual indication of pressure when filling !!
 