I hope someone can clarify if I have diagnosed the fault that I think Ive got.
A few days ago the central heating started to operate in a strange way. The only way to get the pump to turn on was to have the hot water turned on at the timer. And have the cylinder stat calling for heat.
I believe the problem that I have is that the mid position valve is not working properly and is not energising the orange wire as it should. To test this I have removed the valve wires from the house circuit and done the following to see how the valve reacts.
Blue connected to neutral, earth to earth then I energised white and grey as follows and monitored the voltage on the orange wire and noted the position of the valve.
White_Grey___Orange__Position
__X____X_______X_______W
__/____X___see below___M
__/____/___see below___M
__X____/_______X_______W
X=not energised
/=energised
W= Port B (hot water
M= Port A&B (mid position/both)
H= Port A (central heating)
ignore the lines (_) they are just to space out the table
The voltage on the orange wire was 240v as the valve moved to position M but then it fell to around 82v. And the valve never made it to the H position (ie the central heating position) even though I think it should when the grey and white wires are both energised?
My wiring is (I'm fairly certain) as shown on page5 of the following pdf,
http://www.screwfix.com/sfd/i/cat/pdf/20/p4734620.pdf
the valve is a acl-drayton 679H340-30LO
Any help or advice appreciated.
Cheers
Neale
A few days ago the central heating started to operate in a strange way. The only way to get the pump to turn on was to have the hot water turned on at the timer. And have the cylinder stat calling for heat.
I believe the problem that I have is that the mid position valve is not working properly and is not energising the orange wire as it should. To test this I have removed the valve wires from the house circuit and done the following to see how the valve reacts.
Blue connected to neutral, earth to earth then I energised white and grey as follows and monitored the voltage on the orange wire and noted the position of the valve.
White_Grey___Orange__Position
__X____X_______X_______W
__/____X___see below___M
__/____/___see below___M
__X____/_______X_______W
X=not energised
/=energised
W= Port B (hot water
M= Port A&B (mid position/both)
H= Port A (central heating)
ignore the lines (_) they are just to space out the table
The voltage on the orange wire was 240v as the valve moved to position M but then it fell to around 82v. And the valve never made it to the H position (ie the central heating position) even though I think it should when the grey and white wires are both energised?
My wiring is (I'm fairly certain) as shown on page5 of the following pdf,
http://www.screwfix.com/sfd/i/cat/pdf/20/p4734620.pdf
the valve is a acl-drayton 679H340-30LO
Any help or advice appreciated.
Cheers
Neale