Hi All,
Finished my DIY complete CH/DHW install a few weeks ago, the boiler was installed by my CORGI plumber. I'll summarise the system:
3 Bed 1930's semi. Worcestor-Bosch 24i System boiler, Conventional DHW cylinder, Danfoss controls with 3 port mid position valve. The valve is located in the airing cupboard in bedroom 3. My CH pipework tees under the bedroom floor, one pipe goes downstairs, the other services upstairs rads. The tee that goes downstair's first port of call is the hall, which has no TRV and a roomstat, every other rad has a TRV. All my "trunk" pipework is 22mm copper, I tee down to 15 for every rad.
After the boiler install I hadn't got round to balancing the radiators. I've been trying to do this a little bit tonight - because I noticed earlier when I switched the heating on (it had been off most the day), most the rads in the house were hot well before the rad in one of the bedrooms (which is the last in the chain). I reasoned that the downstairs radiators were starving the upstairs of heat, so balancing to restrict their flow was in order.
I started with the (non TRV) rad in the hall. I don't have proper pipe thermometers, so my crude approach is two (identical) digital thermometers with the sensors taped to the pipes, and a sleeve of pipe insulation over the top. It may not be calibrated but I reason that for temperature difference readings, it'll do.
Anyway, I found that the (unbalanced) rad in the hall had a 0.5 degree temperature drop, which is unsuprising with the valves wide open. So, I wound them back and now have a 10 degree drop across that rad. All good.
Next radiator to balance is in the lounge. This is the next radiator in the downstairs loop, and it's the biggest radiator in the house (with a 2.4 KW rating). I took the TRV head off, so that the valve is wide open. Attached the thermometers, and found that the temperature drop with both TRV and lockshield wide open was 14 degrees. This suprised me. I thought that with the pump whizzing along, wide open valves would give small temperature drops.
So, my question - is that normal? for really big rads to have a huge drop and consequently no benefit to winding down the valves at all?
Or, if I go on and balance the other radiators, will this one get more flow and hence the temp. drop reduce?
Or, do I need to turn the pump speed up? It's on setting 2 at the moment. The boiler appears to be quite well modulated back - it's not exactly working hard at all.
Or is there anything i'm missing?
Grateful for any help
thanks
Slip
Finished my DIY complete CH/DHW install a few weeks ago, the boiler was installed by my CORGI plumber. I'll summarise the system:
3 Bed 1930's semi. Worcestor-Bosch 24i System boiler, Conventional DHW cylinder, Danfoss controls with 3 port mid position valve. The valve is located in the airing cupboard in bedroom 3. My CH pipework tees under the bedroom floor, one pipe goes downstairs, the other services upstairs rads. The tee that goes downstair's first port of call is the hall, which has no TRV and a roomstat, every other rad has a TRV. All my "trunk" pipework is 22mm copper, I tee down to 15 for every rad.
After the boiler install I hadn't got round to balancing the radiators. I've been trying to do this a little bit tonight - because I noticed earlier when I switched the heating on (it had been off most the day), most the rads in the house were hot well before the rad in one of the bedrooms (which is the last in the chain). I reasoned that the downstairs radiators were starving the upstairs of heat, so balancing to restrict their flow was in order.
I started with the (non TRV) rad in the hall. I don't have proper pipe thermometers, so my crude approach is two (identical) digital thermometers with the sensors taped to the pipes, and a sleeve of pipe insulation over the top. It may not be calibrated but I reason that for temperature difference readings, it'll do.
Anyway, I found that the (unbalanced) rad in the hall had a 0.5 degree temperature drop, which is unsuprising with the valves wide open. So, I wound them back and now have a 10 degree drop across that rad. All good.
Next radiator to balance is in the lounge. This is the next radiator in the downstairs loop, and it's the biggest radiator in the house (with a 2.4 KW rating). I took the TRV head off, so that the valve is wide open. Attached the thermometers, and found that the temperature drop with both TRV and lockshield wide open was 14 degrees. This suprised me. I thought that with the pump whizzing along, wide open valves would give small temperature drops.
So, my question - is that normal? for really big rads to have a huge drop and consequently no benefit to winding down the valves at all?
Or, if I go on and balance the other radiators, will this one get more flow and hence the temp. drop reduce?
Or, do I need to turn the pump speed up? It's on setting 2 at the moment. The boiler appears to be quite well modulated back - it's not exactly working hard at all.
Or is there anything i'm missing?
Grateful for any help
thanks
Slip