Problems with Ariston combi

Joined
28 Nov 2005
Messages
2
Reaction score
0
Location
Staffordshire
Country
United Kingdom
We have a Ariston Dia 24 MFFI CE (about 7-8 yrs old). We are having problems with it igniting. If we turn the heating off and the water temp to minimum it will generally ignite, but if we turn the water temp above halfway then we get a "whooshing" sound from the boiler. We are not able to get the heating on - the red cut out light comes on.

We have drained the system and bled the radiators.

Any help or advice would be appreciated.

Thanks.
 
Sponsored Links
Your problem is probably caused because you drained your system! Why did you do that?

The auto air vent is probably faulty or just closed!

Tony Glazier
 
We had the problem before we drained the system (we did this after reading some posts on this site).

Sometimes it ignites - most of the time it doesn't.
 
Sponsored Links
How much wate rpressure have you? combis dont ignite below .6bar water pressure (system)
 