Dear All...Please can i get some help!
I have a Feroli signma 60 boiler (gas). I have just switched it on today after it being off for 6 months during the summer. electric and gas supply not turned off though..the boiler just not used.
The problem is that the boiler fires up and then cuts out after a second or two. However if i remove a screw or two from the "airtight (inner) casing" thus letting in some air the boiler fires up and continues as good as gold.
When i switch the CH or HW on the fan starts as does the water pump, there is a spark as there is initial ignition then nothing more with regard to the boiler
I have checked the resistance of the gas valve and these are 1500 ohms and 2900 ohms (approx)
On the air pressure switch (with electric connections off) there is no continuty bcontinuity and NC but 200 ohms between C and NC. contacts but the the boiler it seems. instantaneously
Any ideas
Iain[/b]
I have a Feroli signma 60 boiler (gas). I have just switched it on today after it being off for 6 months during the summer. electric and gas supply not turned off though..the boiler just not used.
The problem is that the boiler fires up and then cuts out after a second or two. However if i remove a screw or two from the "airtight (inner) casing" thus letting in some air the boiler fires up and continues as good as gold.
When i switch the CH or HW on the fan starts as does the water pump, there is a spark as there is initial ignition then nothing more with regard to the boiler
I have checked the resistance of the gas valve and these are 1500 ohms and 2900 ohms (approx)
On the air pressure switch (with electric connections off) there is no continuty bcontinuity and NC but 200 ohms between C and NC. contacts but the the boiler it seems. instantaneously
Any ideas
Iain[/b]