Noticed on my neighbours combi today that his PRV discharge pipe simply drops about 18" beneath the boiler (in 15mm copper with 2x45 degree bends) with the opening facing downwards terminating about 18" above the concrete floor. The boiler is sited in his garage and was RGI installed.
I commented that I didn't think it was correct to terminate the PRV in this way, so we checked the (Vaillant) installation manual, which states:
"The dicharge pipework should be as short as possible and installed with a continuous fall away from the boiler. The pipe should terminate in a position which ensures that any discharge of water or steam from the valve cannot create a hazard to persons in or around the premises, or cause damage to any electrical components or external wiring, and the point of discharge should be clearly visible."
There are no electrics in the line of fire, the point of discharge is clearly visible and with the boiler being sited in his gargage and the opening pointing down, I can't see that it creates a hazard to persons in or around the premises. You couldn't accidentally position yourself in front of the opening.
Were the discharge pipe to be routed through the outside wall there is not a single point on the property where somebody could not walk in front or beneath it.
I know that manufacturers installion guides don't always tally with actual regulations, so . . . what's the answer?
I commented that I didn't think it was correct to terminate the PRV in this way, so we checked the (Vaillant) installation manual, which states:
"The dicharge pipework should be as short as possible and installed with a continuous fall away from the boiler. The pipe should terminate in a position which ensures that any discharge of water or steam from the valve cannot create a hazard to persons in or around the premises, or cause damage to any electrical components or external wiring, and the point of discharge should be clearly visible."
There are no electrics in the line of fire, the point of discharge is clearly visible and with the boiler being sited in his gargage and the opening pointing down, I can't see that it creates a hazard to persons in or around the premises. You couldn't accidentally position yourself in front of the opening.
Were the discharge pipe to be routed through the outside wall there is not a single point on the property where somebody could not walk in front or beneath it.
I know that manufacturers installion guides don't always tally with actual regulations, so . . . what's the answer?