Hi Folks,
I've recently installed a 3KW Air Curtain type heater for a friend at their new shop (they had no heating at all and were freezing!).. I am not a qualified Spark however I believe I am competent to be safe. Please do not flame me or this thread about certifications, I am aware that certificates may be required (are these different from the certs for domestic installations??)
What I am asking for in this post is for really two things:
a) Have I contravened any wiring regs and if so have can I bring my work into compliance?
and
b) Options to avoid overloading the circuit - perhaps it's fine but I don't think 15A is enough for 3Kw Appliance + 2x 13A Sockets.
The shop has an old Wylex Consumer Unit with two separate banks of unlabelled fuses (8 each side I think). Unsurprisingly there is no RCD (I'm going to try and suggest that my friend buys some RCD sockets to replace the existing ones).
When establishing which fuse runs the Double 13A Sockets nearest the New Heater, I went straight for the two 30Amp fuses in the box but discovered that the two sockets were actually on a 15Amp fuse. So far as I could see/test, they were not part of a ring and were a radial circuit from the the CU.
At present the circuit is as follows:
15A Fuse in CU --> 2.5mm Grey PVC Black/Red LN+E Cable [approx 3 metres] --> Double 13A Socket --> 2.5mm White PVC Black/Red LN+E Cable [approx 4 metres in PVC Trunking] --> 13AMP Fused Double-Pole Switch with Neon --> 13A Mains Flex --> 2.5mm Choc Block above ceiling --> Heater's Flex.
N.B The bare earths have all been fitted with Green/Yellow sleeving.
There was no simple option to add a dedicated spur from the CU as it appears to be fully populated (although I did not have good access to it and could not remove the cover to see if any of the fuses were unused). Personsolly, I think both of this friend's shops need new CUs, but that's a job to save in case I get myself qualified.
At present the only other load on the circuit is a display case with 4x low wattage halogen display lamps (no more than 200W max load, but they're probably 25W or less each) - These get back to the double-socket via a 4-way extension lead. I have down-graded the fuse in this extension to 5A for the moment.
I have instructed the staff that high current items such as hoovers, kettles or other heaters are not to be connected to the sockets on this circuit and have labelled them accordingly. This is obviously not satisfactory long-term.
So *if* I am correct and the 15A Fuse in question feeds *only* those sockets and the heater then I should be able to up-rate the fuse to at least 20 Amps (poss. 25A ?)
I would like to hear people's opinions about this and what options would be best:
OPTION: I could totally remove the double socket, thus dedicating the 15A line to the Heater (leaving the 13A fused switch inline)
Question: Can anyone think of any reasons this would not be safe or any caveats?
OPTION: I could increase the Fuse Rating....
Question: Given that the wire is 2.5mm all through, what's the maximum safe Fuse rating? (MCB Rating?)
Question: Can I replace a single Wylex fuse with one of their MCBs or must the whole board be done?
Question: Regardless of the cable thickness, what minimum Fuse rating would officially be required to support a 3KW Heater plus two 13A sockets on one spur? (I've seen mention of calculations based on 30% of load above 10A for things like domestic Ovens/Cookers, but I think this heater draws a far more consistent current - Can anyone tell me the formula)
-- Sub-Option: I could also replace the double socket with a single if it would help.
OPTION: I could replace the Double Socket with 5A Round-Pin sockets, perhaps??
Question: Wild idea which would avoid anything but lights being connected - any comments?
Thanks in advance to anyone who replies.
Regards
Jonathan
I've recently installed a 3KW Air Curtain type heater for a friend at their new shop (they had no heating at all and were freezing!).. I am not a qualified Spark however I believe I am competent to be safe. Please do not flame me or this thread about certifications, I am aware that certificates may be required (are these different from the certs for domestic installations??)
What I am asking for in this post is for really two things:
a) Have I contravened any wiring regs and if so have can I bring my work into compliance?
and
b) Options to avoid overloading the circuit - perhaps it's fine but I don't think 15A is enough for 3Kw Appliance + 2x 13A Sockets.
The shop has an old Wylex Consumer Unit with two separate banks of unlabelled fuses (8 each side I think). Unsurprisingly there is no RCD (I'm going to try and suggest that my friend buys some RCD sockets to replace the existing ones).
When establishing which fuse runs the Double 13A Sockets nearest the New Heater, I went straight for the two 30Amp fuses in the box but discovered that the two sockets were actually on a 15Amp fuse. So far as I could see/test, they were not part of a ring and were a radial circuit from the the CU.
At present the circuit is as follows:
15A Fuse in CU --> 2.5mm Grey PVC Black/Red LN+E Cable [approx 3 metres] --> Double 13A Socket --> 2.5mm White PVC Black/Red LN+E Cable [approx 4 metres in PVC Trunking] --> 13AMP Fused Double-Pole Switch with Neon --> 13A Mains Flex --> 2.5mm Choc Block above ceiling --> Heater's Flex.
N.B The bare earths have all been fitted with Green/Yellow sleeving.
There was no simple option to add a dedicated spur from the CU as it appears to be fully populated (although I did not have good access to it and could not remove the cover to see if any of the fuses were unused). Personsolly, I think both of this friend's shops need new CUs, but that's a job to save in case I get myself qualified.
At present the only other load on the circuit is a display case with 4x low wattage halogen display lamps (no more than 200W max load, but they're probably 25W or less each) - These get back to the double-socket via a 4-way extension lead. I have down-graded the fuse in this extension to 5A for the moment.
I have instructed the staff that high current items such as hoovers, kettles or other heaters are not to be connected to the sockets on this circuit and have labelled them accordingly. This is obviously not satisfactory long-term.
So *if* I am correct and the 15A Fuse in question feeds *only* those sockets and the heater then I should be able to up-rate the fuse to at least 20 Amps (poss. 25A ?)
I would like to hear people's opinions about this and what options would be best:
OPTION: I could totally remove the double socket, thus dedicating the 15A line to the Heater (leaving the 13A fused switch inline)
Question: Can anyone think of any reasons this would not be safe or any caveats?
OPTION: I could increase the Fuse Rating....
Question: Given that the wire is 2.5mm all through, what's the maximum safe Fuse rating? (MCB Rating?)
Question: Can I replace a single Wylex fuse with one of their MCBs or must the whole board be done?
Question: Regardless of the cable thickness, what minimum Fuse rating would officially be required to support a 3KW Heater plus two 13A sockets on one spur? (I've seen mention of calculations based on 30% of load above 10A for things like domestic Ovens/Cookers, but I think this heater draws a far more consistent current - Can anyone tell me the formula)
-- Sub-Option: I could also replace the double socket with a single if it would help.
OPTION: I could replace the Double Socket with 5A Round-Pin sockets, perhaps??
Question: Wild idea which would avoid anything but lights being connected - any comments?
Thanks in advance to anyone who replies.
Regards
Jonathan