rad getting hot whilst hw is on

Joined
21 Sep 2004
Messages
2
Reaction score
0
Country
United Kingdom
hi can someone tell me why my bathroom rad (1st one from pump?)is hot whilst the hot water is tured on ,could it be something to do with honeywell 4073a motorised valve?
 
Sponsored Links
its the way you system has been designed some people like to have the towel rail (rad) in bathroom to be on all the time the boiler is running, so it is tied into the hot water (when your ment to have you bath,you get nice warm towels)
 
If it didn`t usually heat up it could be the motorised valve passing slighty allowing just enough water through to heat the closest rad
 
thanks guys for the reponse ,is there a way i can check the motorised valve?
 
Sponsored Links
Yes. First identify which of the side pipes from the 3 port valve goes to the HW and which the CH. From cold(heating), make the HW be heated. The pipe going to the CH shouldn't get hot.
 