Thought it would be better than having three cables wired into the back of the socket, would it be better to just take the spurs off the sockets then like this?Assuming all of this IS a radial circuit it's ok, BUT
Do you really need those junction boxes?
They aren't really a good idea if they are going to inaccessible.
The armoured cable will go to the house fuse box and be wired into a 30ma RCDThe other concern is that all these sockets and any concealed wiring less than 50mm from the surface will need to be RCD protected at 30 mA, yet your diagram suggests just the outside socket is RCD protected.
Should I use a 20amp mcb in the fuse box as I'm using 2.5mm cable?The armoured cable will go to the house fuse box and be wired into a 30ma RCD
No overload protection?The armoured cable will go to the house fuse box and be wired into a 30ma RCD
It doesn't work like that.I'll install all the wiring and sockets myself then get an electrician in to check and connect up to the house fuse box.
The armoured cable will go to the house fuse box and be wired into a 30ma RCD
When you designed the circuit, what did you work out was the Iz of the cable?Should I use a 20amp mcb in the fuse box as I'm using 2.5mm cable?
The armoured cable will go to the house fuse box and be wired into a 30ma RCD
When you designed the circuit, what did you work out was the Iz of the cable?
Yes I have, he's going to check all my wiring over and then connect to the house fuse board then provide a test certificate and register with local councilHave you found an electrician that is happy with your proposed scheme and is happy for 3rd party test and notification of the installation?