Is it against regs or dangerous for two radials to be connected into the same MCB assuming the total load does not exceed the rating of the MCB?
 
Sponsored Links
in principle a branch point at the breaker is no different from a branch point anywhere else.

just a couple of things to bear in mind.

1: make sure any cable is adequately protected (note that overload protection can be downstream of the cable but short circuit protection can't).

2: there is the reg that reasonable steps should be taken to minimise disruption in the event of a fault. IMO that means that you should only double up like this if there is a good reason to do so (e.g. an an existing CU with no space left or new breakers unavailible).
 