Radiators getting hot when hot water only set on programmer

Joined
18 Oct 2006
Messages
126
Reaction score
2
Location
Leicestershire
Country
United Kingdom
Has anybody came across this before.
On a y plan (GW ultimate 50 boiler) when the programmer is set to hot water only the radiators warm up substantially. When set to c/h only the cold warms up slightly but the radiators do warm up.
I am tending to point the finger at the three port valve. Any other thoughts?
 
Sponsored Links
The y plan valve is passing.....always a sure sign summer is coming.
 
Sponsored Links
well if the head is ok and detachable then you can change the body only.
 