Hi,
I have an issue with my central heating whereby the radiators are always warm. The house gets so warm, even at night when both CH and HW are supposed to be off.
The house is 15 years old, it has:
- Ideal Classic FF240 boiler
- Heatrae Sadia Megaflo CL145 cylinder
- Closed system
There are two motorised valves, one for HW and one for CH
There is a digital Honeywell programmable timer... heating on all the time (but controlled by Nest thermostat), HW on twice a day, hour in the morning, hour in the evening.
There are times when the radiators are warm but hot water timer is off and the Nest is not calling for heat.
By warm i mean the boiler is firing.
Other things I've checked:
There is a stat on the boiler which is set to maximum (6). I turned this down to test and and found that with both the CH and HW switched off, the boiler will still fire up if the boiler stat is turned up (to heat up the primary circuit).
I suspect that the CH motorised valve is either playing up or is not wired correctly.
My reason for thinking this is that when the radiators are getting warm (HW and CH set to off), the pipes either side of the valve are hot. Also, the manual level on the valve is 'stiff' it's not loose. When the boiler stops firing, the lever becomes loose.
Can someone please advise what tests I can perform to verify the wiring/function of this valve?
Thanks.
I have an issue with my central heating whereby the radiators are always warm. The house gets so warm, even at night when both CH and HW are supposed to be off.
The house is 15 years old, it has:
- Ideal Classic FF240 boiler
- Heatrae Sadia Megaflo CL145 cylinder
- Closed system
There are two motorised valves, one for HW and one for CH
There is a digital Honeywell programmable timer... heating on all the time (but controlled by Nest thermostat), HW on twice a day, hour in the morning, hour in the evening.
There are times when the radiators are warm but hot water timer is off and the Nest is not calling for heat.
By warm i mean the boiler is firing.
Other things I've checked:
There is a stat on the boiler which is set to maximum (6). I turned this down to test and and found that with both the CH and HW switched off, the boiler will still fire up if the boiler stat is turned up (to heat up the primary circuit).
I suspect that the CH motorised valve is either playing up or is not wired correctly.
My reason for thinking this is that when the radiators are getting warm (HW and CH set to off), the pipes either side of the valve are hot. Also, the manual level on the valve is 'stiff' it's not loose. When the boiler stops firing, the lever becomes loose.
Can someone please advise what tests I can perform to verify the wiring/function of this valve?
Thanks.